Setting your Trace Auto Gen Start Parameters
02-16-2019, 20:16
Post: #14
RE: Setting your Trace Auto Gen Start Parameters
No. You don't have a problem. That's a common scenario. The thing is our dual Trace inverters aren't working in Parallel or Serial fashion using the DB25 pin cable to connect the two. They're simply two independent inverters both charging the battery bank. Inevitably one inverter will transition to float before the other an you'll end up with one in Float and one in Bulk. This condition is somewhat short lived in that the inverter in Bulk should transition when it's bulk/absorption timer expires. If you want to speed up the process you can reach into the Charge menus and decrement the Absorption timer for the inverter still in Bulk. At some point the red LED will go out and the inverter will transition to Float, then you can set the Absorption timer back to it's default of 3 hours.

david brady,
'02 Wanderlodge LXi 'Smokey' (Sold),
'04 Prevost H3 Vantare 'SpongeBob'

"there is no perfect forum there are only perfect forums"