Run AC's from Inverters or not
07-31-2018, 20:27
Post: #19
RE: Run AC's from Inverters or not
And the rest of the story is if the inverters are in Bulk/Absorption charge then the generator is powering the loads, whether air conditioners or other. If the inverters are in Float charge then as I said earlier they supply power to the loads in an attempt to lower the battery voltage which is held at 14V by the 50DN. If you tend to travel with your generator running, as I do, and if you'd like your generator to power your loads while traveling, then one solution is to disconnect AC1 and AC2 prior to departure, which will put your inverters in Bulk charge, and increase the SW4024 Absorption time. As long as the SW4024's are in Bulk/Absorption they're happy with the 14V put out by the 50DN alternator and they won't try to supplement loads.

david brady,
'02 Wanderlodge LXi 'Smokey' (Sold),
'04 Prevost H3 Vantare 'SpongeBob'

"there is no perfect forum there are only perfect forums"